The following sections discuss stepper motor features and specifications in more detail.
The Duet boards use bipolar stepper motor drivers. This means you can use stepper motors suitable for bipolar drive, which have 4, 6 or 8 wires. You cannot use motors with 5 wires, because those are intended to be driven in unipolar mode only. (Some unipolar motors can be made into bipolar motors by cutting a trace on a circuit board.)
Simplest to connect are 4-wire motors. Inside the stepper motor are two coils, each coil having a wire connected to each end. The wire and coil pairs are called a phase. The 4 wires map to the 4 output pins of each stepper driver on the Duet (see below for identifying phases and connecting).
With 6-wire stepper motors, there are still 2 coils, but each coil has a centre tap, effectively cutting the coil in half if needed. This creates an extra wire for each coil. You can choose to run them in half-coil, by leaving two end-wires unconnected, or full coil mode by leaving the centre wires unconnected. See the motor specification to check that your Duet can supply enough current for how you want to wire them.
8-wire stepper have 4 coils, so with two wires per coil, this makes 8 wires. You can run an 8-wire stepper in half-coil (with only 2 coils connected) or full-coil mode, and in full-coil mode you can choose to wire the coils in series or in parallel. There's plenty of other documentation around the internet on how to do this, just make sure that the Duet can cope with the current requirement. Ultimately, we still need only 4 wires to connect to the Duet.
The rated current is the current per phase that the motor can carry continuously with both phases energised. The holding torque is specified at this current.
M906 sets the peak current per phase. When the motor is moving, the current in each phase follows a sine wave. So a peak current equal to the rated current produces half the rated heat in the motor and about 71% of the holding torque. When the motor is at standstill the phase currents do not change. Depending on the rotor position, one phase can carry the full peak current continuously while the other phase carries none. All the heat is then generated in one motor winding and in one set of driver output mosfets.
So use these limits:
We recommend setting the peak current no greater than the rated current. A lower setting, for example 85% of the rated current, keeps the motor cooler. If you set the peak current greater than the rated current, use standstill current reduction (M917) to keep the standstill current no greater than the rated current. For example, a 2A motor can be run at M906 2800 with M917 71, which gives a standstill current of 2A.
Notes:
To get maximum torque out of your motors without overheating them, choose motors with a rated current no more than about 18% higher than the recommended maximum stepper driver current. The driver can then supply 85% of the motor rated current. This gives:
However, if you use motors with lower current (e.g. 1.0 to 1.2A) and 24V power, then the drivers will run cooler.
This is the maximum torque that the motor can provide with both windings energised at full current before it starts jumping steps. The holding torque with one winding energised at the rated current is about 1/sqrt(2) times that. The torque is proportional to current (except at very low currents), so for example if you set the peak current (M906) to 85% of the motor rated current, then the maximum torque will be 85% * 0.707 = 60% of the specified holding torque.
Torque is produced when the rotor angle is different from the ideal angle that corresponds to the current in its windings. When a stepper motor is accelerating, it has to produce torque to overcome its own rotor inertia and the mass of the load it is driving. In order to produce this torque, the rotor angle must lag the ideal angle. In turn, the load will lag the position commanded by the firmware.
You will sometimes see it written that microstepping reduces torque. What this really means is that when the lag angle is assumed to be equal to the angle corresponding to one microstep (because you want the position to be accurate to within one microstep), higher microstepping implies a smaller lag angle, hence lower torque. The torque per unit lag angle (which is what really matters) does not reduce with increased microstepping. To put it another way, sending the motor a single 1/16 microstep results in exactly the same phase currents (and therefore the same forces) as sending it two 1/32 microsteps, or four 1/64 microsteps, and so on.
There are two relevant sizes: the Nema size number and the length. The Nema size number defines the square dimension of the body and the mounting hole positions. The most popular size for 3D printers is Nema 17, which has a body no more than 42.3mm square and fixing holes in a square of side 31mm.
Nema 17 motors come in various lengths, ranging from 20mm long "pancake" motors to 60mm long motors. As a general rule, the longer a motor is, the greater its holding torque at rated current. Longer stepper motors also have greater rotor inertia. All Duets should be able to drive these, though some Nema 17 motors can be rated up to 2A, which is at the limit of the Duet 2 Maestro (though you can always run motors with less current).
Nema 23 motors offer higher torque than Nema 17 motors. The Duet 2 (WiFi and Ethernet) can drive them if you choose them carefully, in particular in respect of rated current, up to a maximum of around 2.8A. Duet 3 6HC/3HC should be able to drive larger motors, up to 5.5A. You should use 24V power on Duet 2, and 32V power on Duet 3 6HC/3HC for larger motors.
Nema 34 motors are even larger, with more torque, and generally used in CNC applications. Duet 3 6HC/3HC can drive these motors too, up to 5.5A. To achieve high speeds with large motors, you may need higher voltages than the 32V maximum for the Duet 3 6HC/3HC. It is possible to modify the Duet 3 6HC/3HC to increase this to 48V, and possibly 60V (which is the limit of the stepper driver), though this will invalidate your warranty; see this forum thread.
There are two common step angles: 0.9 and 1.8 degrees per full step, corresponding to 400 and 200 steps/revolution. Most 3D printers use 1.8 deg/step motors.
Aside from the obvious difference in step angle:
The inductance of the motor affects how fast the stepper motor driver can drive the motor before the torque drops off. If we temporarily ignore the back emf due to rotation (see later) and the rated motor voltage is much less than the driver supply voltage, then the maximum revs/second before torque drops off is:
revs_per_second = (2 * supply_voltage)/(steps_per_rev * pi * inductance * current)
If the motor is driving a GT2 belt via a pulley, this gives the maximum speed in mm/sec as:
speed = (4 * pulley_teeth * supply_voltage)/(steps_per_rev * pi * inductance * current)
Example: a 1.8deg/step (i.e. 200 steps/rev) motor with 4mH inductance run at 1.5A using a 12V supply, and driving a GT2 belt with 20 tooth pulley would start losing torque at about 250mm/sec. This is the belt speed, which on a CoreXY or delta printer is not the same as the head speed.
In practice the torque will drop off sooner than this because of the back emf caused by motion, and because the above doesn't allow for the winding resistance. Low inductance motors also have low back emf due to rotation.
What this means is that if we want to achieve high speeds, we need low inductance motors and high supply voltage. For the maximum recommended supply voltage, see the board specification pages for your Duet mainboards, expansion and tool boards.
These are simply the resistance per phase, and the voltage drop across each phase when the motor is stationary and the phase is passing its rated current (which is the product of the resistance and the rated current). These are unimportant, except that the rated voltage should be well below the power supply voltage to the stepper drivers.
When a stepper motor rotates it produces a back emf. At the ideal zero lag angle, this is 90 degrees out of phase with the driving voltage, and in phase with the back emf due to inductance. When the motor is producing maximum torque and is on the verge of skipping a step, it is in phase with the current.
Back emf due to rotation is not normally specified on the data sheet, but we can estimate it from this formula:
approximate_peak_back_emf_due_to_rotation = sqrt(2) * pi * rated_holding_torque * revs_per_second / rated_current
The formula assumes that the holding torque is specified with both phases energised at the rated current. If it is specified with only one phase energised, replace the sqrt(2) by 2.
Example: consider a 200 step motor driving a carriage via a 20 tooth pulley and GT2 belt. That's 40mm movement per rev. To achieve a speed of 200mm/sec we need 5 revs/sec. If we use a motor with 0.55Nm holding torque when both phases are driven at 1.68A, the peak back emf due to rotation is 1.414 * 3.142 * 0.55 * 5/1.68 = 7.3V.
How accurate is this formula? dc42 measured and then calculated the back emf for two types of motor:
If you have a target travel speed for your printer, you can work out at least approximately what supply voltage you will need to the motor drivers. Here's how, with an example calculation:
In my example, this gives 32.5V, which is above the 25V recommended input voltage for the Duet 2. But at least we know that for a worst-case delta move with 200mm/sec travel speed, if I use a 24V supply then that is more than 2/3 of the theoretical value, so the torque available for that move should not drop off by more than about 1/3 of the usual torque available. On the other hand, a 12V supply would clearly be inadequate - which explains why I was only able to achieve 150mm/sec before I upgraded the printer to 24V.
There is an online calculator to do this the other way round (i.e. work out the speed at which torque starts to drop off): EMF Calculator.
Selecting an appropriate extruder stepper motor and gearing for the best performance is a compromise between weight, torque, resolution and acceleration.
An extruder drive should have sufficient torque to push the filament through the nozzle at the printing speed you want to use, and sufficient resolution so that individual extruder microsteps are not visible in the print. When there is a Bowden tube between the extruder drive and the hot end, you also need sufficient acceleration to retract the filament fast quickly enough to avoid blobs.
You can calculate the force that an extruder drive can provide before it skips steps if you know its steps/mm and the characteristics of the stepper motor it uses. If using a 1.8deg/step motor, the extruder force in Newtons (N) is:
Extruder_force_at_rated_current = Motor_holding_torque * Extruder_steps_per_mm * 0.0014
For a 0.9deg/step motor:
Extruder_force_at_rated_current = Motor_holding_torque * Extruder_steps_per_mm * 0.0007
where the extruder steps/mm is specified at 16x microstepping, and the motor holding torque is specified in Ncm with both phases energised at the rated current. The steps/mm take into account the gearing (if any) and the diameter of the hobbed shaft.
For 1.75mm PLA filament extruded through a 0.4mm or 0.4mm nozzle, aim for extruder force in the range 10N to 25N at rated motor current, and aim to run at 50% to 85% of rated motor current. For 3mm filament, aim for 3 times the extruder force, so between 30N and 75N at rated current.
If you have too little extruder force, the extruder may not be able to push the filament through the nozzle except at excessively low print speeds or at high print temperatures (which increases stringing). The problem with too much extruder force is that if the nozzle becomes temporarily obstructed, then you want the extruder to skip steps. If instead it grinds an indentation into the filament, then extrusion won't restart when the obstruction is removed.
These typically have steps/mm of about 100 using 1.8/deg motors @ x16 microstepping. To reach 10N force, you need a motor with 71Ncm force. Very few Nema 17 motors have this amount of torque, so you will probably have to make do with 60Ncm, giving a maximum 8.4N force.
The low steps/mm makes it more likely that individual steps will be visible in the extruded filament. With 1.75mm filament and a 0.4mm diameter nozzle, 100 steps/mm going in gives about 5 steps/mm in the extruded filament. You can use a 0.9deg motor to double the steps/mm.
An un-geared extruder design can also be used with a stepper motor with an integral planetary gearbox of about 5:1 ratio.
As well as having gearing, a geared extruder normally has a hobbed shaft with a smaller diameter than an un-geared extruder, because the hobbed insert doesn't have to fit over the stepper motor shaft. Typical steps/mm around 420 with 3:1 gearing, and 650 with 5:1 gearing. This means that you need only about 17Ncm of motor torque to exceed the target 10N force (for 1.75mm filament) with 3:1 gearing, or 11Ncm using 5:1 gearing.
Beware of using motors that have many times too much torque. You can reduce the motor current to reduce the force, however high torque motors also have high rotor inertia, so by reducing the current you also reduce the available acceleration.
These typically have gearing of 30:1 to 40:1 and steps/mm of around 4200.