From RepRapFirmware 3.6, Duet 3 mainboards 6HC, 6XD and Mini 5+ support RS485 serial data transmission standard and the Modbus RTU (Remote Terminal Unit) protocol. These can be used to interface with a wide range of devices, including sensors, relays, Programmable Logic Controllers (PLCs), Variable Frequency Drives (VFDs) and other devices.
Duet 3 Mainboard 6HC v1.02c and later, and Duet 3 Mainboard 6XD v1.02 and later, have an RS485 adapter built-in. For Mini 5+ and older versions of 6HC and 6XD, external RS485 transceivers can be used.
Image: A Duet 3 Mainboard 6XD v1.02 connected to a Modbus RTU temperature and humidity sensor, using the built-in RS485 adapter.
RS485 is a serial communication standard, and is one of the most widely used. It has a number of advantages over other standards that make it particularly suitable for noisy industrial areas.
Modbus RTU (Remote Terminal Unit) is a communications protocol in industrial automation, recognised for its simplicity and efficiency in allowing reliable communication between devices over serial connections such as RS485, and is widely supported.
Modbus RTU works on a master-slave architecture. Each Modbus message follows a structured format consisting of an address field, function code, data field, and checksum. The master initiates a request, specifying the starting address and required Modbus registers, while the slave responds with the requested data. The protocol supports both RTU communication (binary encoding for efficiency) and ASCII mode (human-readable but slower).
Note that the Duet mainboard is the master device, and can not be configured as a slave device.
Diving further into the specifics of the Modbus RTU protocol is beyond the scope of this documentation. There are many guides available, for example see Modbus RTU: A Comprehensive Guide to Understanding and Implementing the Protocol
Duet 3 Mainboard 6HC v1.02c and later, and Duet 3 Mainboard 6XD v1.02 and later, with an RS485 adapter built-in:
For other Duet 3 boards with external RS485 transceivers
Configure the firmware to use the RS485 transceiver with M575, where:
Add one of the following examples to config.g:
M575 P2 B9600 S7 ; enable RS485 on serial channel 2 (io1), baud rate 9600bps, mode 7 (device/Modbus)
M575 P2 B9600 S7 C"io1.out"; enable RS485 on serial channel 2 (io1), baud rate 9600bps, mode 7 (device/Modbus), using io1.out to control Tx/Rx switching
The Modbus RTU implementation in RepRapFirmware uses Gcode to form the Modbus message, so knowledge of the underlying message structure is not generally necessary. You will need your device's documentation to know the device address (usually set to a default initially), the commands supported, and the registers, coils and/or inputs that need to be read or written to.
M261.1 - read data from a device
M260.1 - write data to a device
M260.4 - Raw Modbus transaction
To use the Gcodes, you will need some information on your Modbus RTU device. Generally, the best place for this is the device's datasheet.
In the following sections, an XY-MD01 environment sensor, which measures temperature and humidity, is used as an example. See the picture at the beginning of this page for the wiring setup. You will need to know the Modbus device address, the register you need to read or write to, the values to write, and the Modbus function codes. This is the useful information from the XY-MD01 sensor datasheet:
Product Name: Modbus RTU RS485 SHT20 Temperature Humidity Transmitter
Product Number: XY-MD01
Output signal:RS485 signal
Communication protocol:Modbus RTU and ordinary protocol
Communication address:1~247(default 1)
| Modbus Protocol | ||||
|---|---|---|---|---|
| Function Code | ||||
| Command Register | Function | |||
| 0x03 | Read keep register | |||
| 0x04 | Read input register | |||
| Ox06 | Write a single keep register | |||
| Ox10 | Write more keep registers | |||
| Register Type | Register Address | Register Contents | Bytes | |
| Input Register | 0x0001 | Temperature | 2 | |
| 0x0002 | Humidity | 2 | ||
| Keep Register | 0x0101 | Device Address | 2 | |
| 0x0102 | Baud Rate: 0:9600 1:14400 2:19200 |
2 | ||
| Ox0103 | Temperature Correction -10°C~10°C |
2 | ||
| 0x0104 | Humidity Correction -10%RH~10%RH |
2 | ||
Note the numbers for registers and contents are in hexadecimal, but the Gcode parameters are decimal, so some conversion is required.
Use M261.1 to read data from a Modbus RTU device, where the parameters are:
Sending a correctly formed M261.1 command like the following example from the console will receive the data as hexadecimal:
M261.1 P2 A1 R1 B2 F4
Received 00de 0228
This is the temperature and pressure reading from an XY-MD01 sensor. 00de = 222 in decimal, which is divided by 10 to get 22.2°C. 0228 = 552 decimal, which is 55.2% humidity.
From holding/keep registers (ie device settings), where the first register is 0x0101 hex = 257 decimal:
M261.1 P2 A1 R257 B1 F3 ; register for device address
Received 0001
M261.1 P2 A1 R258 B1 F3 : register for device baud rate (2580 hex = 9600bps)
Received 2580
M261.1 P2 A1 R259 B1 F3 : register for temperature correction
Received 0000
M261.1 P2 A1 R260 B1 F3 : register for humidity correction
Received 0000
Or to retrieve all of them at once:
M261.1 P2 A1 R257 B4 F3
Received 0001 2580 0000 0000
Use M260.1 to write data to a Modbus RTU device, where the parameters are:
For example, changing the device address, where the register is 0x0101 hex = 257 decimal:
M260.1 P2 A1 F6 R257 B3
(cycled power)
M261.1 P2 A3 R1 B2 F4
Received 00df 022f
Sometimes a Modbus device may not adhere strictly to the Modbus RTU protocol, or have additional functions or settings that can be accessed by sending special commands. The device datasheet should outline what the device expects, and RepRapFirmware can send these commands using M260.4.
As an example, the datasheet of the XY-MD01 environment sensor shows the following format is required to retrieve the temperature:
| Master Read Temperature Command Frame (0x04) | |||||||
|---|---|---|---|---|---|---|---|
| Device Address |
Function Code |
Starting Address Hi |
Starting Address Li |
Quantity Hi | Quantity Li | CRC Hi | CRC Li |
| 0x01 | 0x04 | 0x00 | 0x01 | 0x00 | 0x01 | 0x60 | 0x0A |
| Response Temperature Value from Slave | |||||||
| Device Address |
Function Code |
Bytes | Temp Hi | Temp Li | CRC Hi | CRC Li | |
| 0x01 | 0x04 | 0x02 | 0x01 | 0x31 | 0x79 | 0x74 | |
From this, you can create the Modbus command using M260.4. The parameters are:
RepRapFirmware will still need the serial port (P parameter) and Modbus device address (A parameter), and will calculate the CRC for you. It will also need to know how many bytes to return from the response (R parameter). Then the B parameter holds the values in hex you want to send, in this example the function code, two bytes for the address, and two bytes for the number of registers to return.
M260.4 P2 A1 B{0x04, 0x00, 0x01, 0x00, 0x01} R4
Received 04 02 00 dd
In this example, after the device address and CRC are checked and removed, we received back the function code, the number of bytes returned, and the two bytes for the temperature.
Generally, you will want to use the data retrieved from the Modbus RTU connected device. RepRapFirmware provides the M261.1 V parameter to read the data into a variable. Note that:
For example, to use the temperature and humidity values returned by a Modbus sensor, first declare a couple of global variables (in config.g):
global temperature = 0
global humidity = 0
Then create a macro which reads the data from the sensor, and sets the global variables. Note that the variable 'modbusResult' only exists within the scope of the macro:
M261.1 P2 A1 R1 B2 F4 V"modbusResult"
set global.temperature = var.modbusResult[0]/10
set global.humidity = var.modbusResult[1]/10
echo global.temperature ^ "°C, " ^ global.humidity ^ "%RH"
Result:
M98 P"0:/macros/Modbus read.g"
21.40000°C, 58.10000%RH
The values can be accessed by the object model, and used by other processes.
This section will be added to as more Modbus devices are connected to Duet mainboards and RRF.
See the example above.
Examples on the Duet3D forum:
Duet 6XD to a Productivity P1-550 PLC.
Duet 6XD to a Mitsubishi FX3u-485ADP-MB PLC with RS485 Adapter, with 60+ SMT PnP Electric Feeders connected to it. See towards the end of the thread.
Duet 6HC with external RS485 transceiver to a Beckhoff CX7080 PLC
Millennium Machines and user @NineMile have made great strides in getting VFDs to talk to RRF via RS485 and Modbus. They have created a "daemon macro framework for RepRapFirmware v3.6+, which helps to implement RS485 Spindle Control, Monitoring and Feedback across different VFD types." See the ArborCTL github repository here for details.